    Default Wiring a mains socket direct to the fuse board?

    Looking for some advice from a spark or anyone that would know the answer, I need to install a mains socket into the cupboard where my fuseboard is, looks easy to do but I was more concerned with best practice and not voiding my home insurance etc.

    Below is a pic with the cover removed. I assume I would kill the power going into the fuseboard using the breakers that are not pictured but are connected to the two grey wires entering the board, connect the neutral and earth to the common blocks at the top and the live cable to the top of the breaker for the ground floor sockets.

    My question is what spec cable should I use? Is this a big no no for insurance purposes? Are my assumptions above correct?

    The socket will only be used for charging a hand held hoover and maybe other low powered devices so I don't think it will affect the rating of the fuse/breaker for that circuit.

    Spoiler:


    Cheers!


  2. #2
    DF Admin Teajunkie's Avatar
    Join Date
    Dec 2009
    Location
    Devon
    Posts
    4,228
    Thanks
    1,827
    Thanked:        1,825
    Karma Level
    568

    Default Re: Wiring a mains socket direct to the fuse board?

    I have done this exact thing for friends and family not sure about insurance but tbh how will anyone know it wasn’t there already?
    I don’t see any problem personally adding a spur off the fuse box to a twin socket as long as your competent enough will be a piece of cake.

    I added a new ring main into our garage for the server and pc etc but because I am running a tumble dryer and a heater I used 16amp twin and earth.
    Have you joined the DF discord server. https://discord.com/invite/YajVGQxDaw

    Thanks to Teajunkie

    evilsatan (24th March 2018)  


  3. #3
    DF VIP Member Nathz29's Avatar
    Join Date
    Feb 2008
    Location
    Manchester
    Posts
    774
    Thanks
    132
    Thanked:        90
    Karma Level
    231

    Default Re: Wiring a mains socket direct to the fuse board?

    Use 2.5mm twin and earth, your consumer unit is a split load RCD unit so make sure you connect the neutral to the correct bar or it'll trip.

    Get a voltage tester to make sure it's not live before you touch it.

    Have to advise that is should be carried out by an electrician etc .


    Sent from my Armor_2 using Tapatalk

    Thanks to Nathz29

    evilsatan (24th March 2018)  


  4. #4
    DF Super Moderator
    evilsatan's Avatar
    Join Date
    Jul 2004
    Location
    Essex
    Posts
    20,079
    Thanks
    1,105
    Thanked:        3,241
    Karma Level
    1541

    Default Re: Wiring a mains socket direct to the fuse board?

    Cheers lads, usually I'd get an electrician out but as the fuse board is in the same location I can run the cable neatly myself and this particular job looks like something I can do in a morning and save a bit of money. Just wanted to ask on here first in case I was missing something or if I absolutely shouldn't touch it. If I have time will nip down screwfix tomorrow.


  5. #5
    DF Super Moderator piggzy's Avatar
    Join Date
    Jul 2014
    Location
    UK
    Posts
    3,540
    Thanks
    3,063
    Thanked:        1,553
    Karma Level
    371

    Default Re: Wiring a mains socket direct to the fuse board?

    I do stuff like this on the odd occasion and no matter how much I check breakers are off, double check with a multi meter etc, I still shit myself a little bit the first time the screw driver touches that first connector ....

  6. #6
    DF VIP Member coin-op's Avatar
    Join Date
    Mar 2001
    Location
    About
    Posts
    2,670
    Thanks
    60
    Thanked:        199
    Karma Level
    451

    Default Re: Wiring a mains socket direct to the fuse board?

    Quote Originally Posted by piggzy View Post
    I do stuff like this on the odd occasion and no matter how much I check breakers are off, double check with a multi meter etc, I still shit myself a little bit the first time the screw driver touches that first connector ....
    Pussy - I regularly work live on stuff like this. It can have its pitfalls though. My oppo was removing some redundant 16 square 3 phase from trunking and cut through the "dead" cables only to find out (afterwards) that they crossed over as they entered the trunking.
    a big boom and flash and the whole board tripped.
    Cheers - Coin-Op


Similar Threads

  1. half board, full board or all inc??
    By steiff1 in forum Going Places
    Replies: 7
    Last Post: 13th April 2011, 07:42 PM
  2. [NEW] Ridley Scott on board to direct Alien prequel
    By big man in forum Movie Talk
    Replies: 7
    Last Post: 1st August 2009, 08:25 PM
  3. Adam Thole's Tilt Board v3 - Schematics and Board Layout
    By Raptor in forum Microsoft Consoles
    Replies: 0
    Last Post: 2nd July 2009, 04:12 AM
  4. Replies: 0
    Last Post: 6th November 2008, 05:40 PM

Social Networking Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •